The iQ-F series PLC (FX5 series) is a major step forward from the previous generation FX3 and before PLCs.  It has a significantly faster bus between modules.

You are unable to simply connect previous FX2N and FX3U series right side modules to the FX5 (iQ-F) PLCs.  

If you have an FX5UC PLC you want to use a FX5-CNV-BUSC, and if you have an FX5U or FX5UJ or FX5S you want the FX5-CNV-BUS.  These are the bus conversion modules.

Anything after the module must be an FX3 series module and the connectable modules are listed below.